When you see two breakers that are tied together it is the same as what we call a two pole breaker. Each Line or hot wire is protected by a breaker. If either line gets too hot, draws too much current, it opens and the breaker. The tie makes both of them open. Your breaker rating is 20 amps in this case, it is not doubled.
Because the circuit is only 20 amps it is not really worth a darn for a sub panel. You would want a much bigger breaker and wire rated for the breaker to make a sub panel.